Discussions on Customers Commissioning (pre- commissioning), Commissioning, Grid /Distribution Code and Capacity Tests Sample Clauses

Discussions on Customers Commissioning (pre- commissioning), Commissioning, Grid /Distribution Code and Capacity Tests. 4.2.1 Notwithstanding anything in the Agreement to the contrary, and without limiting any other obligations of the Customer, the Customer shall not have the right under the Agreement to require the Commissioning Tests be carried out until the Company is satisfied (acting reasonably) that the Contestable Components have been built to standard and are acceptable to the Company. 4.2.2 As soon as reasonably practicable, but no later than sixty (60) Business Days before completion of the Shallow Works Completion Period and in any event no later than the latest date for such meeting specified in the Construction Programme, the Parties shall meet to discuss, in good faith: 4.2.2.1 what pre-commissioning tests, Commissioning Tests and what Grid Code/ Distribution Code tests are required; 4.2.2.2 which Commissioning Tests are to be conducted by each Party, and which Grid Code/ Distribution Code tests the Company reasonably requires to witness and/or requires notification as to the results; 4.2.2.3 any requirements of the Parties which must be met before they can carry out their respective Commissioning Tests and, in the case of the Customer, the Grid Code/ Distribution Code tests; 4.2.2.4 whether there are any distinct parts of the Contestable Components which are capable of being separately Energised; 4.2.2.5 which of one Party's Commissioning Tests must be conducted simultaneously with Commissioning Tests of the other Party; and 4.2.2.6 the Capacity Test if applicable; 4.2.2.7 if applicable, the date on which the Company shall take operational control of the Contestable Components and Terminal Sub-Station (“the Handover Date”). 4.2.2.8 The date on which settings for protection relays will be required Following the meeting, the dates agreed for these tests shall be confirmed in writing within 10 business days of the meeting.
AutoNDA by SimpleDocs

Related to Discussions on Customers Commissioning (pre- commissioning), Commissioning, Grid /Distribution Code and Capacity Tests

  • Synchronization, Commissioning and Commercial Operation 4.1.1 The Power Producer shall give at least fifteen (15) days written notice to the SLDC / ALDC / DISCOM as the case may be, of the date on which it intends to synchronize the Power Project to the Grid System. 4.1.2 Subject to Article 4.1.1, the Power Project may be synchronized by the Power Producer to the Grid System when it meets all the connection conditions prescribed in the Grid Code and otherwise meets all other Indian legal requirements for synchronization to the Grid System. 4.1.3 The synchronization equipment and all necessary arrangements / equipment including Remote Terminal Unit (RTU) for scheduling of power generated from the Project and transmission of data to the concerned authority as per applicable regulation shall be installed by the Power Producer at its generation facility of the Power Project at its own cost. The Power Producer shall synchronize its system with the Grid System only after the approval of GETCO / SLDC / ALDC and GEDA. 4.1.4 The Power Producer shall immediately after each synchronization / tripping of generator, inform the sub-station of the Grid System to which the Power Project is electrically connected in accordance with applicable Grid Code. 4.1.5 The Power Producer shall commission the Project within SCOD. 4.1.6 The Power Producer shall be required to obtain Developer and/ or Transfer Permission, Key Plan drawing etc, if required, from GEDA. In cases of conversion of land from Agricultural to Non-Agriculture, the commissioning shall be taken up by GEDA only upon submission of N.A. permission by the Power Producer. 4.1.7 The Power Producer shall be required to follow the Forecasting and Scheduling procedures as per the Regulations issued by Hon’ble GERC from time to time. It is to clarify that in terms of GERC (Forecasting, Scheduling, Deviation Settlement and Related Matters of Solar and Wind Generation Sources) Regulations, 2019 the procedures for Forecasting, Scheduling & Deviation Settlment are applicable to all solar generators having combined installed capacity above 1 MW connected to the State Grid / Substation including those connected via pooling stations.

  • Commissioning Commissioning tests of the Interconnection Customer’s installed equipment shall be performed pursuant to applicable codes and standards. The ISO and Connecting Transmission Owner must be given at least five Business Days written notice, or as otherwise mutually agreed to by the Parties, of the tests and may be present to witness the commissioning tests.

  • Power Factor Design Criteria (Reactive Power A wind generating plant shall maintain a power factor within the range of 0.95 leading to 0.95 lagging, measured at the Point of Interconnection as defined in this LGIA, if the ISO’s System Reliability Impact Study shows that such a requirement is necessary to ensure safety or reliability. The power factor range standards can be met using, for example without limitation, power electronics designed to supply this level of reactive capability (taking into account any limitations due to voltage level, real power output, etc.) or fixed and switched capacitors if agreed to by the Connecting Transmission Owner for the Transmission District to which the wind generating plant will be interconnected, or a combination of the two. The Developer shall not disable power factor equipment while the wind plant is in operation. Wind plants shall also be able to provide sufficient dynamic voltage support in lieu of the power system stabilizer and automatic voltage regulation at the generator excitation system if the System Reliability Impact Study shows this to be required for system safety or reliability.

  • Traffic Measurement and Billing over Interconnection Trunks 6.1 For billing purposes, each Party shall pass Calling Party Number (CPN) information on at least ninety-five percent (95%) of calls carried over the Interconnection Trunks. 6.1.1 As used in this Section 6, “Traffic Rate” means the applicable Reciprocal Compensation Traffic rate, Measured Internet Traffic rate, intrastate Switched Exchange Access Service rate, interstate Switched Exchange Access Service rate, or intrastate/interstate Tandem Transit Traffic rate, as provided in the Pricing Attachment, an applicable Tariff, or, for Measured Internet Traffic, the FCC Internet Order. 6.1.2 If the originating Party passes CPN on ninety-five percent (95%) or more of its calls, the receiving Party shall xxxx the originating Party the Traffic Rate applicable to each relevant minute of traffic for which CPN is passed. For any remaining (up to 5%) calls without CPN information, the receiving Party shall xxxx the originating Party for such traffic at the Traffic Rate applicable to each relevant minute of traffic, in direct proportion to the minutes of use of calls passed with CPN information. 6.1.3 If the originating Party passes CPN on less than ninety-five percent (95%) of its calls and the originating Party chooses to combine Reciprocal Compensation Traffic and Toll Traffic on the same trunk group, the receiving Party shall xxxx the higher of its interstate Switched Exchange Access Service rates or its intrastate Switched Exchange Access Services rates for all traffic that is passed without CPN, unless the Parties agree that other rates should apply to such traffic. 6.2 At such time as a receiving Party has the capability, on an automated basis, to use such CPN to classify traffic delivered over Interconnection Trunks by the other Party by Traffic Rate type (e.g., Reciprocal Compensation Traffic/Measured Internet Traffic, intrastate Switched Exchange Access Service, interstate Switched Exchange Access Service, or intrastate/interstate Tandem Transit Traffic), such receiving Party shall xxxx the originating Party the Traffic Rate applicable to each relevant minute of traffic for which CPN is passed. If the receiving Party lacks the capability, on an automated basis, to use CPN information on an automated basis to classify traffic delivered by the other Party by Traffic Rate type, the originating Party will supply Traffic Factor 1 and Traffic Factor

  • Scope of Interconnection Service 1.3.1 The NYISO will provide Energy Resource Interconnection Service and Capacity Resource Interconnection Service to Interconnection Customer at the Point of Interconnection. 1.3.2 This Agreement does not constitute an agreement to purchase or deliver the Interconnection Customer’s power. The purchase or delivery of power and other services that the Interconnection Customer may require will be covered under separate agreements, if any, or applicable provisions of NYISO’s or Connecting Transmission Owner’s tariffs. The Interconnection Customer will be responsible for separately making all necessary arrangements (including scheduling) for delivery of electricity in accordance with the applicable provisions of the ISO OATT and Connecting Transmission Owner’s tariff. The execution of this Agreement does not constitute a request for, nor agreement to, provide Energy, any Ancillary Services or Installed Capacity under the NYISO Services Tariff or any Connecting Transmission Owner’s tariff. If Interconnection Customer wishes to supply or purchase Energy, Installed Capacity or Ancillary Services, then Interconnection Customer will make application to do so in accordance with the NYISO Services Tariff or Connecting Transmission Owner’s tariff.

  • Contract Closure Contracting Officer shall give appropriate written notice to Purchaser when Purchaser has complied with the terms of this contract. Purchaser shall be paid refunds due from Timber Sale Account un- der B4.24 and excess cooperative deposits under B4.218.

  • OFFICE OF MANAGEMENT AND BUDGET (OMB) AUDIT REQUIREMENTS The parties shall comply with the requirements of the Single Audit Act of 1984, P.L. 98-502, ensuring that the single audit report includes the coverage stipulated in 2 CFR 200.

  • Start-Up and Synchronization Consistent with the mutually acceptable procedures of the Developer and Connecting Transmission Owner, the Developer is responsible for the proper synchronization of the Large Generating Facility to the New York State Transmission System in accordance with NYISO and Connecting Transmission Owner procedures and requirements.

  • Equipment Testing and Inspection 2.1.1 The Interconnection Customer shall test and inspect its Small Generating Facility and Interconnection Facilities prior to interconnection. The Interconnection Customer shall notify the NYISO and the Connecting Transmission Owner of such activities no fewer than five Business Days (or as may be agreed to by the Parties) prior to such testing and inspection. Testing and inspection shall occur on a Business Day. The Connecting Transmission Owner may, at its own expense, send qualified personnel to the Small Generating Facility site to inspect the interconnection and observe the testing. The Interconnection Customer shall provide the NYISO and Connecting Transmission Owner a written test report when such testing and inspection is completed. The Small Generating Facility may not commence parallel operations if the NYISO, in consultation with the Connecting Transmission Owner, finds that the Small Generating Facility has not been installed as agreed upon or may not be operated in a safe and reliable manner. 2.1.2 The NYISO and Connecting Transmission Owner shall each provide the Interconnection Customer written acknowledgment that it has received the Interconnection Customer’s written test report. Such written acknowledgment shall not be deemed to be or construed as any representation, assurance, guarantee, or warranty by the NYISO or Connecting Transmission Owner of the safety, durability, suitability, or reliability of the Small Generating Facility or any associated control, protective, and safety devices owned or controlled by the Interconnection Customer or the quality of power produced by the Small Generating Facility.

  • Network Interconnection Architecture Each Party will plan, design, construct and maintain the facilities within their respective systems as are necessary and proper for the provision of traffic covered by this Agreement. These facilities include but are not limited to, a sufficient number of trunks to the point of interconnection with the tandem company, and sufficient interoffice and interexchange facilities and trunks between its own central offices to adequately handle traffic between all central offices within the service areas at a P.01 grade of service or better. The provisioning and engineering of such services and facilities will comply with generally accepted industry methods and practices, and will observe the rules and regulations of the lawfully established tariffs applicable to the services provided.